qcroanoke
Sometimes I don't know if I'm the boxer or the bag
- Location
- Roanoke, VA.
- Occupation
- Sorta retired........
I know by code you can't do this unless the panel and breakers are also rated DC.
Got this in a E-mail today.
"We do use the standard Cutler-Hammer BR style panel. 200 A, 120/240V 40 space house panel. Like I said the rating may not be there for DC using a single pole breaker, that's why we use double pole breakers and break both the positive and negative side of the DC circuit.
To the circuit breaker current is current, no matter if it's DC or AC.....
especially in thermo magnetic breakers."
Is this statement correct?
I am asking because I'm running into a brickwall on this.
This is what the customer wants I'm being told. Customer is a POCO and can do as they please.
Is this dangerous?
or is the big deal the fact that the panel is not listed for DC and therefore a NEC violation?
Got this in a E-mail today.
"We do use the standard Cutler-Hammer BR style panel. 200 A, 120/240V 40 space house panel. Like I said the rating may not be there for DC using a single pole breaker, that's why we use double pole breakers and break both the positive and negative side of the DC circuit.
To the circuit breaker current is current, no matter if it's DC or AC.....
especially in thermo magnetic breakers."
Is this statement correct?
I am asking because I'm running into a brickwall on this.
This is what the customer wants I'm being told. Customer is a POCO and can do as they please.
Is this dangerous?
or is the big deal the fact that the panel is not listed for DC and therefore a NEC violation?