I'm performing a redundant failover audit in our data center and need assistance in understanding how line current is determined in an unbalanced delta wye 480/208y transformer.
My known values are as follows:
Primary line currents (taken from metered UPS): A=67.7, B=81.4, C=72.1
Primary power @ UPS: 59.7KW with a 0.96PF
Primary voltage: 480V
Secondary line currents (clamp meter at main breaker after transformer): a=168.6, b=167.2, c=162.3
Wye neutral line current: 15.3A
I'm attempting to mathematically prove how the secondary line currents become the lower primary line currents, so that I can apply the same technique and determine what the currents would look like in a simulated redundant failover situation at the UPS.
Any help is appreciated. Thank you.