The panel response is surprisingly explanatory. But it seems like a low impedance (60 Hz) ground fault path for the SDS will be a low impedance (60 Hz) earth reference, since the primary EGC is earth referenced Is there a need for the SDS to have a low impedance (higher frequencies) earth reference?
I guess the primary feeder EGC could still function as the SDS GEC if it meets the installation requirements for both.
Cheers, Wayne
I guess the primary feeder EGC could still function as the SDS GEC if it meets the installation requirements for both.
Cheers, Wayne