JP23
Member
- Location
- California
A 15KVA dry type 480-240V 3 phase 3 wire dry type delta-delta transformer with secondary OCP is
feeding a single piece of 3 phase 3 wire 240V equipment in a steel building.
There is a 5% convenience x6 tap on the transformer not being used. I listed the code sections that seem
to apply but still leave me with questions as to the interpretations.
1) Is X6 required to be bonded? 250.20 (B) seems to say no.
2) Is a grounding electrode conductor to building steel required to supplement the EGC?
feeding a single piece of 3 phase 3 wire 240V equipment in a steel building.
There is a 5% convenience x6 tap on the transformer not being used. I listed the code sections that seem
to apply but still leave me with questions as to the interpretations.
1) Is X6 required to be bonded? 250.20 (B) seems to say no.
2) Is a grounding electrode conductor to building steel required to supplement the EGC?