Greg Wrenn
Member
This might be small potatoes for this forum but I thought I would ask anyway. I am moving a machine over to a different plant for our company. I am pretty sure the machine was hooked up to a 240 volt bus bar at the original plant. Now it will be hooked up to a 480 volt bus bar. The conflict that I am seeing is that the motor appears to be already wired up for high voltage, 9 lead lines, 3 load lines divided out to 2 wires a piece under 6 different connectors. However there is a step down transformer inside the control panel for the machine, powering the coils and a receptacle, that has jumpers in place for a 240/120 system. The wires are hookup straight out of the motor control starter so it gets its power from the same place as the motor, so now I am trying to figure out if I have been missing something. As far as I can tell the motor would have been running on 240 volt power while it has been wired up for 480