EGCs do not exist on the line side of the service equipment. If you can't bond the neutral, you will need to provide a supply side bonding jumper.It must be bonded, yes. Some POCOs do not allow bonding to the neutral, but through an EGC.
Either way, a single lug space is easy to work with.
As others have stated, you must either bond the neutral to the enclosure or run a SSBJ. The bottom line is all metallic items must be bonded on the supply side of a service disconnect in compliance with 250.92. It is critically important for fire and shock hazards.On a 480/277 400 amp 3 phase service.
Do you need to bond the neutral to ground inside the current transformer box?
The neutral bar only has space for one wire.
I know you know understand the issue, but you know how picky some of us are about NEC terms.Wrong term, right idea. Thanx for the correction.
How would it prevent either?It is critically important for fire and shock hazards.
Well, for example, if the CT enclosure is left electrically floating do to non metallic raceways it could become energized if there is a fault to the enclosure.How would it prevent either?
How would bonding prevent a fire or shock since there is nothing upstream to trip?Well, for example, if the CT enclosure is left electrically floating do to non metallic raceways it could become energized if there is a fault to the enclosure.
More specifically, 0v to the supply neutral, presumed to be ground.One way or another, the transformer enclosure must be held to 0V relative to ground.
While you can try to do that, it does not happen.One way or another, the transformer enclosure must be held to 0V relative to ground.
How would bonding prevent a fire or shock since there is nothing upstream to trip?
Most do, whether it’s in a jack at the pole for a pole mount, or built in fuse holder in a pad mount. Usually over fused, but on a short circuit, usually doesn’t make much difference, it will still blow.Transformers may have overcurrent devices.
Also the damage from a fault will get noticed and dealt with, thus preventing unknown shock hazard. I agree that preventing fires is probably not a reliable benefit.
I have watched more than once service conductors being vaporized without the transformer primary fuse opening. In one case it was not only the service conductors, but the 4" RMC that contained the service conductors.Most do, whether it’s in a jack at the pole for a pole mount, or built in fuse holder in a pad mount. Usually over fused, but on a short circuit, usually doesn’t make much difference, it will still blow.
FIFY. Potential will rise during a fault event.One way or another, the transformer enclosure must be held to 0V relative to ground during normal operation
That is usually an arcing fault, along with poco overfusing the transformer to a point where it will destroy itself before it blows. I replaced a 4000 amp 480 volt feed where lightning struck the transformer, poco threw in larger fuses, turned it back on. 30 minutes later, the lateral was burned off down to ground level before it blew the fuses. That is why ground fault protection is used on large 480 volt systems.I have watched more than once service conductors being vaporized without the transformer primary fuse opening. In one case it was not only the service conductors, but the 4" RMC that contained the service conductors.
The utilities around here do not size to protect the transformer...they only size to prevent a transformer or secondary conductor fault from taking out the next up stream OCPD.That is usually an arcing fault, along with poco overfusing the transformer to a point where it will destroy itself before it blows. I replaced a 4000 amp 480 volt feed where lightning struck the transformer, poco threw in larger fuses, turned it back on. 30 minutes later, the lateral was burned off down to ground level before it blew the fuses. That is why ground fault protection is used on large 480 volt systems.
larger number of customers served the more likely that may be how they do it.The utilities around here do not size to protect the transformer...they only size to prevent a transformer or secondary conductor fault from taking out the next up stream OCPD.