For a 3ph 480/277 Generac generator, I’m seeing that T1/T2 are supposed to be 120v phase to neutral for the built in battery charger. Am I reading that right?
I don’t see a T1/T2 in their 200a rated transfer switch, so there must not be a step down transformer in the ATS.
I’m no where near a step down transformer with this installation, am I going to have to tap the load side of the ATS, install a fused disconnect and provide a 480x120/240 step down transformer to supply the battery charger circuit?
Generator number is RD05034, ATS is RTSW200K3