I assume you mean 208/120V.
While the panel and breakers for a 480/277V are going to be more expensive than 208/120V equipment, the 480/27V could be used for 208/120V. A bit funky but the equipment is certainly rated for the lesser voltage.
I believe you would need signage posted that states a different voltage is being supplied.
Will anything happen in the long run? Will the breaker trip on time?
While the panel and breakers for a 480/277V are going to be more expensive than 208/120V equipment, the 480/27V could be used for 208/120V. A bit funky but the equipment is certainly rated for the lesser voltage.
Those breakers are going to be real expensive compared to 208/120.
I think I would make the supplier send the correct panel and swap it out. May be able to just swap out the guts. The difference in price of a 277V, 20 amp breakers and a 120V 20 amp breaker starts to add up quick if you have a panel full of breakers.
How can we use a 480/277V square d NF panelboard instead of a 120/208V panelboard. I specified 120/208V panelboard in the drawing. But square D shipped 480/277V panelboard, and the electricians installed it.
I have the same thing at my plant. 480/277V panelboard running 208/120V service. I brought it up after substantial completion and basically everyone said that it as long as it was not a violation of the NEC we were going to have to live with it.
If you decide to leave it installed, it should be very clearly labeled as 208/120V.
But square D shipped 480/277V panelboard, and the electricians installed it.
The only reason I can think of is that the manufacturer shipped a wrong panelbaord
We have used 480Y/277 volt panels for 208Y/120 volt circuits when the engineer wanted 65 KA interrupting rating circuit breakers. GE Type TEY CB's are rated for 65 KA @120 volts.
Interesting. I'm sure that must throw some people for a loop when they see it. :lol:
You have never noticed say an I-Line panel used for 208?
Those are rated 600 volts
Interesting. I'm sure that must throw some people for a loop when they see it. :lol:
The first time I saw it, I opened up the panel board looked at the single pole 277 volt breakers, pulled the panel schedule out of its sleeve and was very, very concerned. Once I tested all the outlets on the panel schedule and found 120 v, I calmed down a little bit. But yes, it threw me for a loop for about 10 minutes.