We are replacing lamps, ballasts and sockets in a parking lot. We are replacing 1000W MH with a newer, lower wattage lamp/ballast. The site voltage is 480, but the manufacturer only makes a 277V ballast and is sending a step down transformer to mount at each fixture. I feel the transformer is not rated high enough, that it needs to be 125% of the each lamp/ballast load. He says he does this all the time (hope not). Am I wrong code wise? I couldn't find the exact code reference that would say this. I found the overcurrent section. Somewhere in the back of my mind I remember you could load a trans. 100% but don't really use them in the work I do. I couldn't find the exact code reference that would say this. I found the overcurrent requirements.
Thanks
Thanks