This 480/480-277v, delta-wye xfrm was wired backwards and nobody caught it until start up. After energizing, all the voltages were reading ok.(primary and secondary voltages) At the lighting panel 476v phase to phase. 268/270 phase to ground. After we energized a lighting load the lights were blinking. The plant electrician checked voltage at the breaker and saw 480v phase to neutral. We turned the circuit off and checked voltage. Now with no load we read 476 phase to phase, 166 phase to ground. Why wouldn't we have seen this before turning on a lighting load.