the motor will have to draw more amps. to produce the rated output power.
It goes without saying that the motor's nameplate full-load amps (FLA) rating cannot be exceeded, therefore, as in the case of VFD control of a motor, it is understood that a motor that is "oversized" for the load will be required.
Doug's question is, as I read it, - by how much? I recommend that the motor manufacturer be consulted.
Provided the setting (or heater selection) for the motor's overload relay is based on the nameplate FLA and Service Factor (SF) ratings, the windings would be protected from overheating no matter which voltage/hertz it is operated at.
However, some motors are not suitable for use with a VFD due to balance problems, and reduced cooling fan efficiency.
Ed