X xformer Senior Member Location Dallas, Tx Occupation Master Electrician Jun 2, 2014 #2 D.robin said: can they be spliced in same j-box Click to expand... Look at 300.3C
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Jun 2, 2014 #3 As long as the wires are clearly identified (color, tape, tag or whatever) according to voltage system, I do not see a problem. Tapatalk!
As long as the wires are clearly identified (color, tape, tag or whatever) according to voltage system, I do not see a problem. Tapatalk!
iwire Moderator Staff member Location Massachusetts Jun 2, 2014 #4 D.robin said: can they be spliced in same j-box Click to expand... Yes
kwired Electron manager Location NE Nebraska Occupation EC Jun 2, 2014 #5 They are all in the same "compartment, space, box, etc. in a typical 480 - 208 transformer, whether it be a unit with lugs or a unit with just wire leads to connect to.
They are all in the same "compartment, space, box, etc. in a typical 480 - 208 transformer, whether it be a unit with lugs or a unit with just wire leads to connect to.