It's been a while since I've dealt with this issue, so wanted to make sure my calculations are correct.
I need a 200A secondary feed per phase off a transformer. The load will be a large number of 120v servers for a temporary installation.
The primary side is 480v delta.
Right now we're looking at a 75kVA transformer which by:
75000 / (208 x 1.73) = 208A. That seems like we are right on the edge here. Given the type of load does 75kVA sound large enough? This is for a temporary installation so pushing the envelope a little bit is okay, but I want to make sure it is safe and capable.
Thanks.
I need a 200A secondary feed per phase off a transformer. The load will be a large number of 120v servers for a temporary installation.
The primary side is 480v delta.
Right now we're looking at a 75kVA transformer which by:
75000 / (208 x 1.73) = 208A. That seems like we are right on the edge here. Given the type of load does 75kVA sound large enough? This is for a temporary installation so pushing the envelope a little bit is okay, but I want to make sure it is safe and capable.
Thanks.