On a 480 v corner grounded to transformer 120/208 Y is the grounded leg of 480 v delta always bonded to the frame of the transformer.
On a 480 v corner grounded to transformer 120/208 Y is the grounded leg of 480 v delta always bonded to the frame of the transformer.
No, you never rebond a grounded conductor
So the grounded leg on a delta 480 v to 120/208 v is always bonded to the transformer ?
No.
If you have a corner grounded supply to any transformer you do not bond the grounded supply conductor again. It is already bonded at its source.
There is a difference between a grounded conductor and an EGC. The grounded conductor is only connected to the grounding conductor at one point....at the main bonding jumper for a service or at the system bonding jumper for a separately derived system.What about a EGC from the source to the transformer housing ?
There is a difference between a grounded conductor and an EGC. The grounded conductor is only connected to the grounding conductor at one point....at the main bonding jumper for a service or at the system bonding jumper for a separately derived system.
The primary EGC must be connected to the transformer non-current carrying parts, but that is not the same as connecting the primary grounded conductor to the transformer non-current carrying parts.
Note, for transformers fed by more than two wires, the case of the transformer being supplied from a corner grounded system. is one of the very few cases where you bring a grounded conductor to the primary terminals of a transformer.
This is the way that I have always looked at it:There is a difference between a grounded conductor and an EGC. The grounded conductor is only connected to the grounding conductor at one point....at the main bonding jumper for a service or at the system bonding jumper for a separately derived system.
The primary EGC must be connected to the transformer non-current carrying parts, but that is not the same as connecting the primary grounded conductor to the transformer non-current carrying parts.
Note, for transformers fed by more than two wires, the case of the transformer being supplied from a corner grounded system. is one of the very few cases where you bring a grounded conductor to the primary terminals of a transformer.
The thing that plays with most minds is that with a corner grounded delta you are grounding a phase conductor
In most cases, yes.Is a neutral a grounded conductor.
Is a neutral a grounded conductor.
The simple answer is yes. It is very common to refer to the grounded conductor as the nuetral.
Technically I would say that a nuetral is always a grounded conductor but a grounded conductor is not always a real nuetral.
Technically a neutral does not have to be a grounded conductor. It is defined in terms of its voltage relationship to the rest of the circuit conductors.
But with very few exceptions the NEC requires that if a neutral exists it must be grounded.
Where does it say that? While it is common to ground the neutral of a 480/277 system, I dont recall it being required like it is required on a 208/120 system.
250.26 appears to contradict that statement.Technically a neutral does not have to be a grounded conductor. It is defined in terms of its voltage relationship to the rest of the circuit conductors.
But with very few exceptions the NEC requires that if a neutral exists it must be grounded.
250.26 applies to systems that are to be grounded, i.e. if the system is to be grounded, it shall be the neutral that is grounded.250.26 appears to contradict that statement.
On a 480 v corner grounded to transformer 120/208 Y is the grounded leg of 480 v delta always bonded to the frame of the transformer.