I am building panels that require 1 ammeter for each motor in the panel. The motors only draw 4.8 amps, so I purchased 0 - 10Amp Shurite meters and CT's. I found the Shurites can take the current without a CT. This brought up many questions that I can't find good answers to......
1. Code says you have to run all three conductors together. If I would run one leg through the ammeter on the door, I would think the other legs would also have to go to the door.
2. With three motors, thats 12 lines of 480 on the door, doesn't feel the safest. But if I use my 10:1 CT with 10 wraps on the primary (to get the 1:1), I would only need 6 wires on the door with 0 volts each.
3. If a wire were to break or come loose, the door would have a wire with 4,800 volts on it. That doesn't seem safer.
So, my one discovery about the ammeter being able to take the 480 current without a CT has made me unsure about the whole idea of panel door mounted ammeters. What is best / safest practice in this situation?
1. Code says you have to run all three conductors together. If I would run one leg through the ammeter on the door, I would think the other legs would also have to go to the door.
2. With three motors, thats 12 lines of 480 on the door, doesn't feel the safest. But if I use my 10:1 CT with 10 wraps on the primary (to get the 1:1), I would only need 6 wires on the door with 0 volts each.
3. If a wire were to break or come loose, the door would have a wire with 4,800 volts on it. That doesn't seem safer.
So, my one discovery about the ammeter being able to take the 480 current without a CT has made me unsure about the whole idea of panel door mounted ammeters. What is best / safest practice in this situation?