I have a 150,000 sq foot warehouse wanting to convert over to 277 volt lighting from 480..how would I figure the new load....this is an exam question. ..that's all they told me
Well I figured the warhose at 1/4 VA/SQ foot that's what I thought the lights should be figured at..I'm not sure where you get 3 VA sq foot..maybe I'm looking at something wrong
Question as posed is not answerable since incomplete.I have a 150,000 sq foot warehouse wanting to convert over to 277 volt lighting from 480..how would I figure the new load....this is an exam question. ..that's all they told me
Not sure what they are shooting for but to maintain the same level of lighting the "load" would not change in terms of "kw". 220.12 calls for 3 watts per sq ft lighting load and that's respective of voltage. Table 220.42 will allow a demand factor.
If i did the math correctly the result would be 231.25kw at any voltage.
I have a 150,000 sq foot warehouse wanting to convert over to 277 volt lighting from 480..how would I figure the new load....this is an exam question. ..that's all they told me
I agree.Question as posed is not answerable since incomplete.
Yes but I'm testing oregon...im good with tests but this one was tough on the calculation part...very frustrated
Well,it's an exam question. I'm sure many of us have seen questions that have little bearing on real life situations.The new load in kva would be the same as the old load in kva. Other than that more information is needed. Just changing from 480 to 277 doesn't has any obvious purpose.