We have a broadcast transmitter to install than can accept up to @ 440V. The manufactuer says 480V is not acceptable, and that 416 is the max preferred.
The utility says they cannot provide 416, but only 277/480 WYE (or otherwise something lower in the <240 range.
What sort of transformer do we need to suggest to the building prefrabricator should be researched to go from 480 (possibly Delta) to 416 WYE?
We realize this will need to be further reviewed by an electrical contractor or PE, but we are getting nowhere with the client's inhouse engineer, so we have to move the information dialog along.
Thank you