frenchelectrican
- Nord'est Wisconsin et Paris France
hello guys and ladies :
i ran into a good question about using 1600 amp switchboard what i try to find the correct wire size for this appaction ;
5 parelleal cables size 750 MCM will meet the nec code ? or 600 MCM copper and yeah the type will be thhn or xple ( super tough service enterince cable ) and from switchboard to transformer it is 75 meter ( 260 feet) long so if that meet the code i have older code book chart but dont say over 1200 amps so i try to figured out for 1600 amps and it have 5- 4 inch pcv conducts there and the extra one for spare
p.s i will list the motors
3- 150 hp
2- 100 hp
2- 50 hp
5- 20 hp
mixed bags of motors total sum of 20 hp
and i got the figured it came out 1,083 amps so let me know
thanks for your time
merci marc
3- 150 hp
2- 100 hp
2- 50 hp
5- 20 hp
merci marc