480 V delta / Y HRG System - Unusual LN Voltages

Merry Christmas
Status
Not open for further replies.

rls4183

Member
posted August 07, 2003 09:31 PM
--------------------------------------------------------------------------------
I work in the paper industry and recently we have experienced unusual voltages on one of our 480 V systems. The system is feed from a delta/Y HRG XFMR. We are currently reading the following line to ground voltages: A=550V, B=770V, C=950V. These voltages have been checked with a digital and analog meter. We have found the HRG on the XFMR to be burnt up and we assume that it is open, thus giving us an ungrounded system. I can see where you could get 480V to ground on this system now because of this issue, but don't have much of an explanation for these voltages. One thing to note on this issue is that this XFMR is paralled with another delta to Y XFMR. This XFMR however is ungrounded and has a hard ground on one phase of this system (A phase to Ground = 5 Volts). Someone stated that with these 2 systems being ungrounded now, that somehow we are measuring through multiple sets of windings on these systems. I can't see this be/ both XFMR's are delta to Y and I thought that this would eliminate circulating currents?? Another theory on what is going on is there is an arcing ground on this now ungrounded system and that this ground is causing capacitive charging on this system, thus causing the higher voltages. I am not familiar with capacitive charging. Can anyone help??
 

charlie

Senior Member
Location
Indianapolis
Re: 480 V delta / Y HRG System - Unusual LN Voltages

Anytime you have an ungrounded secondary, the reading to a ground reference does not mean anything. The voltage relationship between the phases will still be correct and functional. It is possible for your AC to actually be riding on a DC or static component that you meter is measuring.

Reestablish the HRG and the problem will take care of itself. ;)
 

templdl

Senior Member
Location
Wisconsin
Re: 480 V delta / Y HRG System - Unusual LN Voltages

I guess you could consider that the ungrounded Wye would give similar line to ground voltages as are commonly found with ungrounded deltas.
 

charlie

Senior Member
Location
Indianapolis
Re: 480 V delta / Y HRG System - Unusual LN Voltages

Originally posted by templdl:
I guess you could consider that the ungrounded Wye would give similar line to ground voltages as are commonly found with ungrounded deltas.
You are exactly right. In fact, if you do not use the center point of a 480Y/277 volt bank for a neutral conductor, you do not have to ground it and you can use the three phases as an ungrounded "delta". Additionally, you may corner ground one of the phases.
 