I'm not sure what you are asking. Maybe this:
Starting with the assumption you are discussing 480/277 grounded Y:
The neutral has to be brought to at least the first disconnect. It has to be bonded and grounded at least at one point. The reason for this is so the system can supply (and return) sufficient ground fault current to reliably, quickly trip protective CBs.
The NEC may also require the neutral to be bonded and grounded in two places. But this is a legal issue - has nothing to do with physics, good design practice, or safety
Any requirement for the neutral to go beyond the first disconnect depends on if the system has any 277V loads. If it does, then the neutral must be carried out to the last 480/277V panel.
A lot of industrial installations do not carry the neutral past the first disconnect. If there are any 277V loads out in the field, a small 480D/480Y xfm is installed to feed a local panel board. The 480Y secondary neutral is bonded and grounded just like it was a service.
Your questions are good - keep asking.
carl