I have a 480 V VFD to run a 208 V pump. Sugestions??
... although some vfds will allow you to set the incoming voltage as low as you want, but they are not real common.
Although you can technically do that, it is REALLY REALLY bad for the motor windings. If the supply is 480V, the DC bus level is 679V, which means each pulse going to the motor is at that level. The VFD can adjust the PWM pattern to deliver only 208V RMS, but that will still be made up of short little 679V DC pulses, probably exceeding the insulation level of the motor windings and causing premature failure.
A VFD controls the RMS output voltage by just changing the length of time the DC bus is connected to the output?
Pretty much.So am I understanding this correctly?
A VFD controls the RMS output voltage by just changing the length of time the DC bus is connected to the output?
Provided the VFD is rated at the motor current, there is no problem.I have a 480 V VFD to run a 208 V pump. Sugestions??
So am I understanding this correctly?
A VFD controls the RMS output voltage by just changing the length of time the DC bus is connected to the output?