W wobblybob Member Location Lancaster, Pa, USA Jul 2, 2019 #1 Is a 480 volt 3 phase delta connected system always required to be grounded? Sent from my iPhone using Tapatalk
Is a 480 volt 3 phase delta connected system always required to be grounded? Sent from my iPhone using Tapatalk
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jul 2, 2019 #2 For 3Ø, 3 wire no, take a look at 250.20(B).