I am wiring an area of a manufacturing shop. Currently they have 480 volt 30 amp branch circuits fed from a Buss duct to a cord drop.This cord drop feeds a welding booth, a lifting table that draws 4 amps, an exhaust fan on top of the booth that draws 4.5 amps and a fan used for employee cooling in the summer. 30 amps carries the load but my question is do these small motors require a fused disconnect for each motor. The 2 fans each have a motor starter as does the lifting table. There is a 30 amp receptacle for each piece of equipment. also the so cord used for each piece of equipment is currently 16-4. Is this sized correctly?. Would it make a difference if it was a 20 amp circuit. what code sections would explain how to do this. There are other 480v 30a circuits that feed only the cooling fans. Can these be plugged into a 30a receptacle with no fusible disconnect?