Our company is adding a small chiller a SAC-05. They apparently bought it from an oversees vendor with poor manuals and communication skills.
It comes with a whip/ cord with a premade cord l1-l2-l3 neutral and gnd.
Looking at the diagram it uses one leg of the 3 phase and the neutral to supply a transformer 280-220 step down for control power like I would suspect to be a wye system.
Can I replace the transformer with a 480-240 volt transformer being fed by L1-L2 because we run a ungrounded 480v delta?
The Motors are foreign and use no neutral for the hook up from the diagram.
Is there a difference between a wye and delta motor because from my guess from the control power this is normally used with a wye system?
Do to lack of knowledge or language skills the vendor cannot answer the questions
Thanks as always
Dave