Good Morning
I went out and looked at a problem for a friend yesterday. The electrical contractor had installed a 480-volt, 3 phase, 60 amp Square D contactor that drove an air-circulating fan. He had told me that the fan would not kick in upon closing the control ckt. The coil voltage was 120 volt and the control ckt distribution was right next to the controller. ( no voltage drop, voltage was nominal when metered). Anyhow, with the control ckt closed, X2,(neutral) was not feeding through and providing potential at the contactor coil terminals. Upon going through the old, faded schematic on the cover, I think the neutral side has a N/C contact point that might have some sort of overload protection. It sure seems like it, as the X2 side has a line and load terminal. It has a field landed terminal and a factory landed terminal that has a factory lead going to the contactor proper. Problem is, it just looked like a clear plastic terminal point built into the mechanism of the contactor. I only looked at it for a minute or two, but nothing really jumped on how to even take it out.
A couple of questions:
Do most contactors have an overload that is factory built in for the control side, I know this is an extremely general question but how about for the type of contactor I have described above. And why on X-2? I have seen them before when the contactor has a X-form, but with this gear, you have to bring it it.
If this is some sort of overload, IE, bi-metal strip or similar, where would the reset be? The front cover had a square black reset button in the middle of it, but this is for resetting the overloads for the motor itself that are installed in the contactor.
How common is it, to have control circuits built into the neutral (grounded) conductor of these control devices?
I am trying to find some information on the contactor, (explosion view or other) so I can just learn a little more
Also, I have been digging around in the code and trying to see if it is some sort of code violation not to have this contactor identified that it has two different voltages installed in the same enclosure. I will try and send a picture, If the picture goes through, the X-2 terminal is on the bottom and I installed the wirenut to by-pass the the terminal points to see if the contactor would close. It did so the problem is a N/O point at that terminal.
I went out and looked at a problem for a friend yesterday. The electrical contractor had installed a 480-volt, 3 phase, 60 amp Square D contactor that drove an air-circulating fan. He had told me that the fan would not kick in upon closing the control ckt. The coil voltage was 120 volt and the control ckt distribution was right next to the controller. ( no voltage drop, voltage was nominal when metered). Anyhow, with the control ckt closed, X2,(neutral) was not feeding through and providing potential at the contactor coil terminals. Upon going through the old, faded schematic on the cover, I think the neutral side has a N/C contact point that might have some sort of overload protection. It sure seems like it, as the X2 side has a line and load terminal. It has a field landed terminal and a factory landed terminal that has a factory lead going to the contactor proper. Problem is, it just looked like a clear plastic terminal point built into the mechanism of the contactor. I only looked at it for a minute or two, but nothing really jumped on how to even take it out.
A couple of questions:
Do most contactors have an overload that is factory built in for the control side, I know this is an extremely general question but how about for the type of contactor I have described above. And why on X-2? I have seen them before when the contactor has a X-form, but with this gear, you have to bring it it.
If this is some sort of overload, IE, bi-metal strip or similar, where would the reset be? The front cover had a square black reset button in the middle of it, but this is for resetting the overloads for the motor itself that are installed in the contactor.
How common is it, to have control circuits built into the neutral (grounded) conductor of these control devices?
I am trying to find some information on the contactor, (explosion view or other) so I can just learn a little more
Also, I have been digging around in the code and trying to see if it is some sort of code violation not to have this contactor identified that it has two different voltages installed in the same enclosure. I will try and send a picture, If the picture goes through, the X-2 terminal is on the bottom and I installed the wirenut to by-pass the the terminal points to see if the contactor would close. It did so the problem is a N/O point at that terminal.