R romero07 New member Nov 9, 2004 #1 when your service is 480 volt delta system.Is it required that one of the phases should be bonded to ground.
when your service is 480 volt delta system.Is it required that one of the phases should be bonded to ground.
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Nov 9, 2004 #2 Re: 480 volt delta system Only if it meets any of the conditions in 250.20(B).
J jtester Senior Member Location Las Cruces N.M. Nov 12, 2004 #3 Re: 480 volt delta system John is correct that the NEC doesn't require grounding. Some utilities will, and some authorities such as MSHA will want grounding or at least ground fault monitoring.
Re: 480 volt delta system John is correct that the NEC doesn't require grounding. Some utilities will, and some authorities such as MSHA will want grounding or at least ground fault monitoring.