I'm hoping some one can help me with this - In the Northeast until about the 1970 most water and sewage pump stations were fed with either a 240 or 480 volt Delta voltage with the "B" phase being grounded. These systems are not being supported by the utilities any more and when they fail they are generally replaced with a wye system. We are doing a small upgrade in a water pumping station that has a 100 amp. 480 volt service with the "b" phase grounded.
The main circuit breaker is a 3 pole 100 amp unit in it's own enclosure that feeds a small Main lugs only distribution panel that is single phase. The center phase in grounded inside a CT cabinet (that is technically owned by the utility)that is located between the Main C/B and the distribution panel. The grounded phase is terminated on the neutral bar. The grounded phase wire has been color coded white.
My questions are:
What would be the most correct colors for the individual phases?
Inasmuch as this is a water pump station should the service be grounded to the water main as well as the existing driven ground?
Currently the branch circuit ground conductors are terminated on the neutral bar. Shouldn't they be installed on a separate ground bar?
Hopefully I got this into the correct forum.
Thanks for your help..
The main circuit breaker is a 3 pole 100 amp unit in it's own enclosure that feeds a small Main lugs only distribution panel that is single phase. The center phase in grounded inside a CT cabinet (that is technically owned by the utility)that is located between the Main C/B and the distribution panel. The grounded phase is terminated on the neutral bar. The grounded phase wire has been color coded white.
My questions are:
What would be the most correct colors for the individual phases?
Inasmuch as this is a water pump station should the service be grounded to the water main as well as the existing driven ground?
Currently the branch circuit ground conductors are terminated on the neutral bar. Shouldn't they be installed on a separate ground bar?
Hopefully I got this into the correct forum.
Thanks for your help..