I need to get power to a machine in a weld shop. The building is supplied with 480v delta. There is a 480v bus duct that runs along where the machine is going to be installed. Power supply line has to be large enough to handle 245 full load amps at 480v, 3 phase, 60 hertz. Main circuit breaker in control 300 amps. Maximum short circuit interruption capacity of the main circuit breaker 30,000 amps.
In the specs it says the three phase power configuration must be a symmetrical 4 conductor WYE line supply network with a grounded neutral point. For all other line supply types (3 wire Delta), a customer supplied isolation transformer with a grounded neutral point on the secondary side is required.
This would be my first 480 Delta to 480/277 Wye install. Could anyone help me on this one? Anything different than 480 Delta to 208/120 Wye.
Do I need Transformer fault sensing installed?(in the form of donut type current transformers?)
In the specs it says the three phase power configuration must be a symmetrical 4 conductor WYE line supply network with a grounded neutral point. For all other line supply types (3 wire Delta), a customer supplied isolation transformer with a grounded neutral point on the secondary side is required.
This would be my first 480 Delta to 480/277 Wye install. Could anyone help me on this one? Anything different than 480 Delta to 208/120 Wye.
Do I need Transformer fault sensing installed?(in the form of donut type current transformers?)