wharehouse
Member
- Location
- Northern Ca
Hello all, new here and need a bit of info, appreciate the input. Does a battery charger labeled 480 volt single phase need to be fed with A and B phase from a 480 volt 4 wire system ? Also is there a code violation feeding this equipment using 2 poles only on a 3 pole single trip 20 amp breaker ? The battery charger is for an electric forklift and is labeled for 208/240/480 volt, since there is a 277/480 volt panel available, the load would be approx 11.5 amps at 480 volts. It was supplied with a 2 pole/w ground blade type cord cap, rated to 50 amps. Am I limited to the length of the supply cord,within reason, using cord cap as disconnect, to a hard piped condiut and receptacle within 8 feet of panel. ? ...btw ,all equipment is 2006 year model...
thanks again,
thanks again,