480-volt, three-phase, deadman leg

Status
Not open for further replies.
Came across something I have never seen before, 480-volt three-phase service in an old industrial part of town. Service has three legs and ground, when checking voltage I got 480-volts between L1 &L2, L1 & L3, L2 & L3. L1 to ground 480-volts L3 to ground 480-volts
L2 to ground 1.3 volts, power company came out and said all is good, how could this be? Any one else ever see this? how can I be getting 480-v to ground on 2 legs/
 
Came across something I have never seen before, 480-volt three-phase service in an old industrial part of town. Service has three legs and ground, when checking voltage I got 480-volts between L1 &L2, L1 & L3, L2 & L3. L1 to ground 480-volts L3 to ground 480-volts
L2 to ground 1.3 volts, power company came out and said all is good, how could this be? Any one else ever see this? how can I be getting 480-v to ground on 2 legs/
It looks like you have a corner grounded delta, often called a Grounded B phase system.

Remember ground is simply a reference point, therefore any one conductor can be grounded. This is why the NEC, in article 250 uses the term 'grounded' conductor and not 'neutral'.
 