I have a question that's was brought up to me... There is an electric engineer that is giving my customer a hard time about installing his equipment.
The customer has equipment and HVAC that runs on 120/240 volt single phase.
The power supply is from a 800 amp MDP 277/480 volt 3 phase panel.
We would normally install a 2 pole 100 amp 480v breaker to feed a 480v/120/240 volt single phase transformer 50kva.
The electrical engineer is saying that it can not be done that way. Because it will not be a balanced load. He says it will cause he 3 phase panel to now be unbalanced and has concerns about the neutral in his 480 volt panel?
Can you give me some insight on this please. I am not sure if I should just install a 3 pole 480 volt 3 phase breaker to feed a 480volt to 120/240 volt 3 phase 50 KVA and only use the A and C phase off the transformer to feed my 120/240 volt single phase panel?
My customer can not change any of his equipment.
The customer has equipment and HVAC that runs on 120/240 volt single phase.
The power supply is from a 800 amp MDP 277/480 volt 3 phase panel.
We would normally install a 2 pole 100 amp 480v breaker to feed a 480v/120/240 volt single phase transformer 50kva.
The electrical engineer is saying that it can not be done that way. Because it will not be a balanced load. He says it will cause he 3 phase panel to now be unbalanced and has concerns about the neutral in his 480 volt panel?
Can you give me some insight on this please. I am not sure if I should just install a 3 pole 480 volt 3 phase breaker to feed a 480volt to 120/240 volt 3 phase 50 KVA and only use the A and C phase off the transformer to feed my 120/240 volt single phase panel?
My customer can not change any of his equipment.