L leon2012 Member Location Marietta Ga 30067 Oct 11, 2012 #1 Is it ok to run 3 480 volt wires with a 120 V circuit in a 3/4 EMT pipe?
roger Moderator Staff member Location Fl Occupation Retired Electrician Oct 11, 2012 #2 In most case yes, if they are emergency circuits and non emergency circuits the answer would be no. Roger
In most case yes, if they are emergency circuits and non emergency circuits the answer would be no. Roger
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 12, 2012 #4 Are all of the conductors power circuit conductors?
D DARUSA Senior Member Location New York City Oct 13, 2012 #5 leon2012 said: Is it ok to run 3 480 volt wires with a 120 V circuit in a 3/4 EMT pipe? Click to expand... As long that both insulation are rated for the maximum voltage!! In this case 480 volt (thhn is rated for 600volts)
leon2012 said: Is it ok to run 3 480 volt wires with a 120 V circuit in a 3/4 EMT pipe? Click to expand... As long that both insulation are rated for the maximum voltage!! In this case 480 volt (thhn is rated for 600volts)
petersonra Senior Member Location Northern illinois Occupation engineer Oct 14, 2012 #6 There is no general prohibition on mixing voltages in a conduit. There are some requirements that may come into play though that might have an impact on a specific installation. Previous posters have mentioned some of them.
There is no general prohibition on mixing voltages in a conduit. There are some requirements that may come into play though that might have an impact on a specific installation. Previous posters have mentioned some of them.