480V 1Ph 3-wire water heater!

Status
Not open for further replies.

bhawghead

Member
Location
Panama City, Fl
Occupation
Automation Technician
Hello, new guy here, one of our engineers recently purchased an 80gal. water heater for a temporary project and it is 480V 1Ph 3-wire, and our facilities tech. has wired it to a 480V 3ph disconnect. I am not involved with the project, but I just thought this to be a rather odd wiring for a water heater and it doesn't seem correct to be wired to a 3ph disconnect. Been reading posts from this site off and on for reference purposes and just thought I would get your professional opinion.
 
I guess my only concern would be how he wired it thru the 30A Hubbell plug(2 hots and a ground) I know basically this is the same principal as 240V, with 2 hots and a ground, but the engineer is saying he should have put in a transformer.......the facilities tech told him no, and wired it up to the disconnect using So cord and a 30A Hubbell plug. I agree with the Tech our engineer doesn't seem to be understanding. I think I should have explained this better in my original post.
 
Yes, thank you. I understand this, our Tech understands this, our engineer unfortunately does not! I have tried to explain this to him but I'm not getting thru.
 
Most of the manufacturer catalogs I have don't even show a single pole 480v fusible or non-fusible disconnect and some note to use a 3 pole in lieu of a 2 pole.
 
UL tests multi-pole breakers and fusible disconnects using the possible combinations of pole configurations. This is why manufacturers rarely offer 'heavy duty' 480V switches with less than 3 poles. The little potential sales volume does not make up for the cost of additional testing and inventory control.
 
I agree with the others but its always helpful if you can post a photo of the nameplate so we can be sure.
 