BackCountry
- Southern California
- Licensed Electrician and General Contractor
Gentlemen, this is confusing me and after reading each post on 250.30(a)(1) exception no. 2 I’m even more confused. Single line diagram is attached.
Scenario:
480v 3ph 4w service into a three pole fused disconnect. Neutral and GEC are bonded in the fused disconnect (service entrance) and the neutral stops there, nothing in this installation requires a neutral derived from the service (all 480v, no line to neutral 277v used). This is mounted to a wooden panel board at the property line.
From the fused disconnect, three 3/0 CU feeders (phase A and B, third conductor is at present bonded to ground and serves as an EGC) go underground 400’ to three 480x120/240 step down transformers, all on phase A and B, obviously not balanced. Those transformers all serve different buildings on this site, and have a neutral to case bond at the step down transformer. They also have ground rods bonded.
We will be installing a 480v 50kw generator between the service panel board and the step down transformers. We will also be installing a large PV array. As part of the project, we will balance the three step down transformers and restore phase C.
The million dollar question is:
Do I need an EGC from the service entrance to the step down transformers if there is no neutral anywhere used? I really don’t want to yank out those 3/0 CU feeders and repull an EGC, I’d love to take the third 3/0 conductor and make that phase C. I’m not real up on grounding a conductor and using it as an EGC, your help is appreciated.
Scenario: