Step by step of electric
- Dfw
- Electrician
I have a client of mine which invited me to bid for power distribution in his warehouse, his warehouse has a 1900amp siemens switch board which i will need to provide a 500 ft run from the switchboard to designated power distribution, Is it proper for me to install 3 sets of 2 1/2 emt conduit with 400 mcm alumminum wire with a 1/0 copper gu wire .
From the 480v distribution panel i will need to feed a 225kva transformer i know that at 480v i get 271 amps which i will need to multiply 125% for continuous load
which gives me 338 A and my next standard size is 350 amps is this correct because i have a supposed electrical engineer that works in the facilily that says "breaker size of the step-down transformer to 250A. Breaker protection for transformer should not be more than it's capacity"
what primary side size conductor at 75c is necessary to feed a 225kva transfomer in parallel.
thank you!
thank you!