480V breaker on a 240V system

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Greetings,
Can one use a 480V, 3 pole breaker on a 240V, 3 phase system? Is that kosher?
How would that affect the kAIC rating of the unit?

Appreciate the help on this one.
Thanks,
EE
 
We have used 480 and 277 volt CB's on 208Y/120 volt panels when the engineer specified a high 65 KAIC rating. Something like this:
65KAIC Circuit Breaker.jpg
 
And generally, the 240V IC rating is higher than the 480V rating, like in this case:
GE-Breaker-Label.jpg

25kAIC @ 480V, 65kAIC at 240V
 
Yeh I’ve used NF PowerLogic 480 panelboards on 208Y/120 systems .


Sent from my iPhone using Tapatalk
 