Can one use a 480V, 3 pole breaker on a 240V, 3 phase system? Is that kosher?
How would that affect the kAIC rating of the unit?

Appreciate the help on this one.
Thanks,
EE
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We have used 480 and 277 volt CB's on 208Y/120 volt panels when the engineer specified a high 65 KAIC rating. Something like this:
65KAIC Circuit Breaker.jpg
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
And generally, the 240V IC rating is higher than the 480V rating, like in this case:
GE-Breaker-Label.jpg

25kAIC @ 480V, 65kAIC at 240V
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
Yeh I’ve used NF PowerLogic 480 panelboards on 208Y/120 systems .