Junior_EE
Member
- Location
- New York City
Because of supply chain issues, a client is looking to select a 480V chiller despite our building having only 208V. Obviously we need a step-up transformer to accommodate the load.
Here is the info on the chiller @ 480V from the manufacturer:
359A MCA
600A MOPD
In order to size the breaker and wires for this on the 208V side of the step-up transformer, is it simply
MCA @ 208V = 359A * 480V / 208V = 829A?
MOPD @ 208V = 600A * 480V / 208V = 1384A? --> 1400A
Further, on the secondary of the step-up transformer, do I just supply 359A worth of wire to the chiller with 600A circuit breaker? I feel a little leery about having wire ampacity lower than the breaker on a transformer secondary.