dm9289
Industrial Maintenance Electrician
- Location
- Pennsylvania
- Occupation
- Industrial process repair/ maintenance Electrician
In my plant we had a 1955 crane retrofit with a new wireless control system due to many wiring and contactor problems. The contractors only re-utilized the motors and house ungrounded 3 delta 480v connection rails (new high temp wire and festoon system). The hoist and trolley are reversing contactor type, the bridge is a drive to give us different speeds.
We almost always use gloves while using the crane but a day after the contractors left we were lowering their junk and an employee took his glove of due to having some problem getting used to the control buttons (wireless) while holding the hoist wire rope standing on a metal frame and got shocked.
We called the contractor back and found during certain different bridge positions the voltage to the wire rope would vary from 0 volt most of time to up to 120v. During our last use of this frequently unused crane ( used mainly during annual 1 week maintenance project) it did toast a contactor blew some fuses and we noticed wiring in need of replacement. The contractors believe the shock it is due to a bad motor which seems likely.
Finally to the questions
Our old school electric buyer wants to replace the motor as suggested but also wants to replace the drive due fear that regenerative voltage is causing the problem. Does this make sense to replace the drive with contactors?
The contractor in addition to replacing the motor suggested adding a 4th rail for a gnd to eliminate the shock hazzard in the future. The old school buyer does not want to add the rail due to cost and feels the cranes metal wheels on our building should be adequate. Does anyone agree with this being an adequate gnd system?
Short of a 4th rail does anyone have any ideas or experience with grounding this sort of crane short of adding a 4th rail?
We almost always use gloves while using the crane but a day after the contractors left we were lowering their junk and an employee took his glove of due to having some problem getting used to the control buttons (wireless) while holding the hoist wire rope standing on a metal frame and got shocked.
We called the contractor back and found during certain different bridge positions the voltage to the wire rope would vary from 0 volt most of time to up to 120v. During our last use of this frequently unused crane ( used mainly during annual 1 week maintenance project) it did toast a contactor blew some fuses and we noticed wiring in need of replacement. The contractors believe the shock it is due to a bad motor which seems likely.
Finally to the questions
Our old school electric buyer wants to replace the motor as suggested but also wants to replace the drive due fear that regenerative voltage is causing the problem. Does this make sense to replace the drive with contactors?
The contractor in addition to replacing the motor suggested adding a 4th rail for a gnd to eliminate the shock hazzard in the future. The old school buyer does not want to add the rail due to cost and feels the cranes metal wheels on our building should be adequate. Does anyone agree with this being an adequate gnd system?
Short of a 4th rail does anyone have any ideas or experience with grounding this sort of crane short of adding a 4th rail?