Hey guys so I'm new to the industrial setting and don't fully understand 480v delta systems. Any help would be appreciated
Hey guys so I'm new to the industrial setting and don't fully understand 480v delta systems. Any help would be appreciated
Thank you. I appreciate itGo to the link below and look at all the different Delta threads, it's a good place to start.
https://www.electrical-contractor.n...php/forums/15/1/technical-reference-area.html
Roger
Are you about to go to work in a 480V Delta system? It's becoming more rare every day, because utilities don't really want to supply it any more, they prefer 480Y277V and if you want a Delta, you have to ask for a variance.
The purpose of using a delta system stems back mainly to WWII when defense related industries were asked to run at capacity full tilt with as little shutdown as possible, even at risk of life and limb. I like to describe it as a "Damned the torpedoes, full speed ahead!" attitude. That's because in an ungrounded delta system, a line-to-ground fault does NOT cause the system to shut down, you simply move from an ungrounded delta to a corner grounded delta system, and everything keeps running. So you had some sort of ground indication system that let the electricians know there was a ground fault somewhere, but generally you didn't know exactly where at first, you had to go find it. When I started back in the late 70s at a steel mill, that's what we had. We had three light bulbs on the wall and if one glowed brighter than the other two, that phase had a ground fault somewhere and we would jump in a golf cart to run around looking for smoke, or a production manager running around pulling his hair out because his machine stopped running.
But some time in the 80s, the NEC stopped allowing ungrounded delta systems unless you added ground fault PROTECTION, not just indication, OR you used a corner grounded delta system; one or the other. Both options however removed the "Damned the torpedoes..." benefit of using a delta system anyway, so it fell out of favor. Even later it became evident that delta systems are really unkind to power electronics, such as VFDs, UPS systems, large DC power supplies etc., and that became the final death knell for utilities offering it without a thorough vetting of why you want it and how it will be implemented.
So if you are going to work somewhere that uses a 480V delta system, it's going to be either a corner grounded delta, or there will be a GFP system involved that can shut down your entire system, and if you have any VFDs etc., you will need to pay a lot of special attention to how you connect and protect them. If this is just out of curiosity, you may never see one in your career.