Below is from a research paper I was reading. Question---if your distrusting 480v why do you need a transformer for a 277v piece of equipment. Thanks
Understand that it is much more efficient to distribute 480V than 120V. The later you derive 120V in the dis- tribution, the higher your efficiency will be. (Distribute at greater than 480V if you can specify a higher voltage service). Two other tips are:
Use small 480-480/277V transformers to derive 277V as needed. Typical uses for 277V are lighting and HVAC reheat boxes (both available in 480V). Before specifying 480V, ensure the style you need is available in that voltage and you?ve addressed maintainability issues.Understand that it is much more efficient to distribute 480V than 120V. The later you derive 120V in the dis- tribution, the higher your efficiency will be. (Distribute at greater than 480V if you can specify a higher voltage service). Two other tips are:
Use small (e.g., 15KVA) 480-120/208V transformers to derive 120V near the load, to shorten 120V runs. For a factory, think of 480/277V as feeding the infrastructure (e.g., HVAC, lighting, elevators, plant air) and produc- tion equipment and 208/120V as feeding controls and offices. For a commercial building, think of 480/277V as feeding the infrastructure, and 208/120V as feeding everything else.