We have a situation whereby we have to feed a 480V fire pump from a 208V service through a step-up transformer. Does the following setup comply with code?
Fire Pump HP: 40HP
Fire Pump FLA: 52A (480V)
Step-up Transformer KVA: 52 x 480 x 1.73 = 43.2kVA (45kVA is too close, use 75kVA)
Fire pump feeder on secondary side of the transformer: 52 x 1.25 = 65A (6 AWG)
Fire pump current on the primary side of the transformer: 43.2/(208x1.73) = 120.3 A
Fire pump feeder on the primary side of the transformer: 120.3 x 1.25 = 150.4A (2/0 AWG)
Fire pump OCPD on primary side of the transformer: 120.3 x 6 = 721.8A (next size up 800A)
The fire pump OCPD will be fed from the 208V utility service transformer. It is my understanding that the OCPD on secondary side of the transformer is not required in this situation.