circuitrider
Member
- Location
- Upstate SC
I admit that I'm looking for a loophole for a very type design, but I have a 400A bus available and I need to know if I can make it code legal. Using Table 430.250 for all of my 480V loads for FLA: 100% of all motors plus 25% largest motor plus 125% of continuous non-motor load equals 402 A. (There are no noncontinuous non-motor loads.)
Several of the motors are anywhere from 1/6 to 1/3 horsepower, but I used 1.1 A since 1/2 hp is the smallest size on the table. Is there anything that will allow me to use smaller FLAs for these smaller motors and therefore not have to split some of these loads to a different bus?
Several of the motors are anywhere from 1/6 to 1/3 horsepower, but I used 1.1 A since 1/2 hp is the smallest size on the table. Is there anything that will allow me to use smaller FLAs for these smaller motors and therefore not have to split some of these loads to a different bus?