Table 110.26(A)(1) Working Spaces
Minimum Clear Distance
Nominal Voltage to Ground Condition 1 Condition 2 Condition 3
0–150 900 mm(3 ft) 900 mm (3 ft) 900 mm (3 ft)
151–600 900 mm (3 ft) 1.1 m (3? ft) 1.2 m (4 ft)
Note: Where the conditions are as follows:
Condition 1 — Exposed live parts on one side of the working space and no live or grounded parts on the other side of the working space, or exposed live parts on both sides of the working space that are effectively guarded by insulating materials.
Condition 2 — Exposed live parts on one side of the working space and grounded parts on the other side of the working space. Concrete, brick, or tile walls shall be considered as grounded.
Condition 3 — Exposed live parts on both sides of the working space.