When feeding a 480V 3 Phase panelboard, is the feeder sized for the load on the panelboard or the panelboard rating? Also what percentage would the feeder breaker and cable be sized for?
 

pasha

Member
Re: 480V Panelboard

The feeder is always sized not on the load condition but on the panel board rating + 30% of the breaker rating.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 480V Panelboard

Originally posted by pasha:
The feeder is always sized not on the load condition but on the panel board rating + 30% of the breaker rating.
Where did the 30% come from? :confused:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 480V Panelboard

Originally posted by pasha:
The feeder is always sized not on the load condition but on the panel board rating + 30% of the breaker rating.
What????

Roger
 
Re: 480V Panelboard

Now I am only a 1st Year Apprentice but alas I do spend a quite a bit of time in my code book wanting to be a good Electrician. Art. 215 on Feeders

215.2 (A)(1) Can't list what acutally says because of copyright.

But wouldn't it fall under this in code? Which basicaly says size for load (as calculated in 220 on branch circuits) if non-continuals and 125% if continuous.

Thanks just trying to figure out myself where +30% came from.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: 480V Panelboard

This section of the Mike Holt NEC Frum relates to code. The code answer is that the feeder is sized for the load. gvmv has the correct code reference. The feeder must be sized for 100% of the non-continuous load plus 125% of the continuous load. The rating of the panelboard does not enter into that equation.

Now let us digress: set the NEC book aside, and enter the design world. I would recommend sizing any panel?s feeder to handle the rating of the panel. If you have a 225 amp panel, then give it 225 amp?s worth of feeder. Note that you don?t have to size the feeder for 125% of the panel rating. The design process should not permit the calculated load (for that panel) to go beyond 100% of the non-continuous load plus 125% of the continuous load. All this is, of course, a design consideration. It is intended to support future expansion. More to the point, it goes beyond code requirements, in order to make the customer happy.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 480V Panelboard

Amen charlie. If I see a 200 amp panelboard, I would expect its good for 200 amps. the service entrance conductors are only sized to the calculated load. You can round up to the next standard size OCPD. If my load is calculated at 175.6 amps, I can round up to 200 amp disconnect as long as the conductors are sized for 175.6 amperes.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: 480V Panelboard

...215.2 (A)(1) Can't list what acutally says because of copyright.

Huh? Anybody ever had the NFPA threaten them with copyright infringement because they quoted an article here? This is a code forum, and it would be kind of tough to discuss the NEC without verbatim quotes and I think the NFPA realizes that.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 480V Panelboard

There is fair use of copyrighted material, its ok to quote limited amounts. If there was a long quote from the NEC I would ask it be edited down. Besides, we should all have the NEC.
 