This section of the Mike Holt NEC Frum relates to code. The code answer is that the feeder is sized for the load. gvmv has the correct code reference. The feeder must be sized for 100% of the non-continuous load plus 125% of the continuous load. The rating of the panelboard does not enter into that equation.
Now let us digress: set the NEC book aside, and enter the design world. I would recommend sizing any panel?s feeder to handle the rating of the panel. If you have a 225 amp panel, then give it 225 amp?s worth of feeder. Note that you don?t have to size the feeder for 125% of the panel rating. The design process should not permit the calculated load (for that panel) to go beyond 100% of the non-continuous load plus 125% of the continuous load. All this is, of course, a design consideration. It is intended to support future expansion. More to the point, it goes beyond code requirements, in order to make the customer happy.