I have an exhaust air handler on a data center. long story short, the fuses on the primary side of controls transformer were blowing so we determined we had a bad transformer. Old transformer was 1500VA 460:120 square d transformer (9070T1500D20). Had a time crunch so I got what I though was the same square d 1500VA transformer but realized it was slightly different (9070T1500D1). New transformer has separate taps for 460V and 480V. We have a 480V system.
Square d customer service says to not use the 460V variety on a 480V system. I was always under the impression that a 460V transformer was a nominal and would cover up to 480V. Trying to determine if we should go through and change all of the old 460V transformers to 480V transformers. Anyone else have experience with this?
Square d customer service says to not use the 460V variety on a 480V system. I was always under the impression that a 460V transformer was a nominal and would cover up to 480V. Trying to determine if we should go through and change all of the old 460V transformers to 480V transformers. Anyone else have experience with this?