So recently a 460V Air compressor was said to be blown(electrical motor).
Here is the info on the motor-
Product line : W40 NEMA Premium Efficiency ThreePhase Product code : 14367176 Catalog # : 04036OT3E286TS-W40 Frame Output Poles Frequency Rated voltage Rated current L. R. Amperes LRC No load current Rated speed Slip Rated torque Locked rotor torque Breakdown torque Insulation class Service factor Moment of inertia (J) Design : 284/6TS : 40 HP (30 kW) : 2 : 60 Hz : 230/460 V : 93.7/46.8 A : 609/304 A : 6.5x(Code G) : 30.8/15.4 A : 3540 rpm : 1.67 % : 59.3 ft.lb : 190 % : 240 % : F : 1.25 : 2.02 sq.ft.lb : B Locked rotor time Temperature rise Duty cycle Ambient temperature Altitude Protection degree Cooling method Mounting Rotation¹ Noise level² Starting method Approx. weight³ : 14s (cold) 8s (hot) : 80 K : Cont.(S1) : -20°C to +40°C : 1000 m.a.s.l. : IP23 : IC01 - ODP : F-1 : Both (CW and CCW) : 73.0 dB(A) : Direct On Line : 339 lb Output 25% 50% 75% 100% Foundation loads Efficiency (%) 91.5 91.7 92.4 92.4 Max. traction Power Factor 0.51 0.76 0.84 0.87 Max. compression Drive end Non drive end Bearing type : 6311 Z C3 6211 Z C3 Sealing : Without Bearing Seal Without Bearing Seal Lubrication interval : 20000 h 20000 h Lubricant amount : 18 g 11 g Lubricant type : Mobil Polyrex EM Notes USABLE @208V 104A SF 1.15 SFA 119A This revision replaces and cancel the previous one, which must be eliminated. (1) Looking the motor from the shaft end. (2) Measured at 1m and with tolerance of +3dB(A). (3) Approximate weight subject to changes after manufacturing process. (4) At 100% of full load. These are average values based on tests with sinusoida
The tech said that there was too much power going to the disconnect to the top of the motor starter. I read the amperage and it read appr- 491V, 495V, 496V leg to leg. each leg to neutral was around 270V. The system says 460. the voltage seems correct but trying to get a second opinion
Here is the info on the motor-
Product line : W40 NEMA Premium Efficiency ThreePhase Product code : 14367176 Catalog # : 04036OT3E286TS-W40 Frame Output Poles Frequency Rated voltage Rated current L. R. Amperes LRC No load current Rated speed Slip Rated torque Locked rotor torque Breakdown torque Insulation class Service factor Moment of inertia (J) Design : 284/6TS : 40 HP (30 kW) : 2 : 60 Hz : 230/460 V : 93.7/46.8 A : 609/304 A : 6.5x(Code G) : 30.8/15.4 A : 3540 rpm : 1.67 % : 59.3 ft.lb : 190 % : 240 % : F : 1.25 : 2.02 sq.ft.lb : B Locked rotor time Temperature rise Duty cycle Ambient temperature Altitude Protection degree Cooling method Mounting Rotation¹ Noise level² Starting method Approx. weight³ : 14s (cold) 8s (hot) : 80 K : Cont.(S1) : -20°C to +40°C : 1000 m.a.s.l. : IP23 : IC01 - ODP : F-1 : Both (CW and CCW) : 73.0 dB(A) : Direct On Line : 339 lb Output 25% 50% 75% 100% Foundation loads Efficiency (%) 91.5 91.7 92.4 92.4 Max. traction Power Factor 0.51 0.76 0.84 0.87 Max. compression Drive end Non drive end Bearing type : 6311 Z C3 6211 Z C3 Sealing : Without Bearing Seal Without Bearing Seal Lubrication interval : 20000 h 20000 h Lubricant amount : 18 g 11 g Lubricant type : Mobil Polyrex EM Notes USABLE @208V 104A SF 1.15 SFA 119A This revision replaces and cancel the previous one, which must be eliminated. (1) Looking the motor from the shaft end. (2) Measured at 1m and with tolerance of +3dB(A). (3) Approximate weight subject to changes after manufacturing process. (4) At 100% of full load. These are average values based on tests with sinusoida
The tech said that there was too much power going to the disconnect to the top of the motor starter. I read the amperage and it read appr- 491V, 495V, 496V leg to leg. each leg to neutral was around 270V. The system says 460. the voltage seems correct but trying to get a second opinion