D depatie73 Member Oct 19, 2005 #1 Is the nuetral considered a current carrying conductor in a 480V and 208V system?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 19, 2005 #2 Re: 480V Maybe...See 310.15(B)(4). Don
S sedeca Member Oct 19, 2005 #3 Re: 480V Depatie73, Art 310.15(B)(4) Neutral Conductor. tells you when to count the neutral as a current carrying conductor
Re: 480V Depatie73, Art 310.15(B)(4) Neutral Conductor. tells you when to count the neutral as a current carrying conductor
bob Senior Member Location Alabama Oct 19, 2005 #4 Re: 480V sedeca Read 310.15(B(4(a) again. depatie73 You asked this same question under your post on "Transformer". Why don't you read 310.15 for your self and get the answer? [ October 19, 2005, 10:55 PM: Message edited by: bob ]