I seem to be going in circles to find a code reference to determine the minimum size main breaker for a multi-starter control panel.
3-20HP 3-phase Blowers FLA 27amps
1-2KVA transformer 480-120 (2000/480=4.17amps)
Each motor has its own circuit breaker, contactor and overload device. The transformer has its own primary and secondary fusing.
I would always size it as:
27+27+27+4.17=85.17
85.17*1.25=106.43amp
therefore: 125amp main breaker minimum.
1. Does this seem right?
2. Is there a code reference that talks about the minimum main breaker size for this application?