My question is about grounding requirements for telecom equipment on a cell tower site. There is a rectifier and battery backup unit (24VDC system). A DC/DC converter then converts the 24VDC to -48VDC for the telecom equipment. The telecom equipment is split so that the part of the equipment at the base of the tower has a power distribution unit that supplies -48VDC to the other equipment up in the tower. The DC cable is shielded and the shield is grounded. So the questions are:
- is this scenario not covered by NEC scope (ie interpretation of 90.2 (B)(4))? Does a cell tower site leased by telcos meet this rule? Are telcos considered communications utilities?
- further on 250.162 (A) interpretation ie is grounding required:
-- is this application considered premises wiring?
-- does the nominal -48VDC system fall under the 50-300V scope?
-- would this application meet Exception No. 2 being a rectifier-derived DC system?
- is a separate ground/neutral wire needed in this application running up the tower in addition to the +/- wires?