What feeder size would I use to feed a 4 gang meter bank that feeds (4) 100A main breaker panels?
Whatever calculated load using art 220 gives you, is the minimum size conductor you can use.What feeder size would I use to feed a 4 gang meter bank that feeds (4) 100A main breaker panels?
220 calculations still determine the minimum size service or feeder permitted.If a may get on my "semantics" soapbox for a minute.. the wording of your question would lend itself toward your wanting to determining a service conductor size in which case kwired's answer is spot on, Art 220.
IF you are truly sizing a feeder then size of the overcurrent device ahead of the feeder would be a determining factor.
220 calculations still determine the minimum size service or feeder permitted.
Those four 100 amp breakers being supplied do not necessarily have to be supplied with 100 amps each, service or feeder doesn't matter, art 220 load calculation is minimum either way.
Bottom line is you still needed to go to art 220 before you can come up with the 820 amps of load.thank you, professor
In his case, yes .. service or feeder same... but my intent was to note to the OP or newbie that proper description can make a difference. Assuming a 820 amp load,if you are sizing a service vs a feeder on a 1000 amp OCP device (standard size over 800), it will make a difference.